    Dear BIOMCH-L members:

    In Dec. of last year I posted a question to the list with respect to
    the planning and design of a new biomechanics facility. The original
    post appears below followed by a list of the responses I received.
    Several of the respondents spent considerable time putting together
    their thoughts and opinions on this topic, and I am grateful for their
    willingness to share both their knowledge and experience about
    technical issues relating to lab planning and design. I hope this
    information will be useful to other members of the biomechanics
    community.


    Original post:

    Dear BIOMCH-L members:

    I have a request to those of you who have been involved in the
    "planning and design" of new biomechanics labs. The Faculty of
    Kinesiology and Health Studies at the University of Regina is currently
    in the process of planning for a badly needed new facility to be
    completed in 2005. I am in the enviable position (I think) of being
    asked for input with respect to how a new biomechanics lab will be
    planned and incorporated into this new facility. I have a very good
    idea what is needed in terms of space and location (ground floor etc.).
    However, what we actually "get" will of course be determined by a
    variety of factors, one of which will be what is common or standard
    (if there is such a thing) in new biomechanics labs that have been
    constructed specifically for that purpose within the last 5 to 15
    years. Essentially I would like to find out what is the "state of the
    art" with respect to the design of new biomechanics labs, if such a
    thing exists. Could those of you who have specific information on the
    design and physical dimensions of recently constructed biomechanics labs
    please send me some information (it need not be lengthy)? Here are some
    specific questions with respect to the type of information I'm
    requesting:

    -dimensions (length x width)
    -location (presumably ground floor for force plates, but also location
    with respect to other facilities; e.g., gymnasium, parking garage, etc.)
    -equipment (i.e., how many force plates - parallel or in
    series, length of walkways, # of cameras, flexibility of
    camera positioning, e.g., overhead, etc.)
    -function (i.e., primary use; e.g., clinical, research, instructional;
    of what type; gait, neuromuscular, isokinetic, etc.; any secondary or
    tertiary functions?)
    -lighting/electrical requirements (e.g., A/V, emergency power, computer
    stations, etc.)
    -structural requirements (e.g., floor, walls, roof, etc.)
    -mechanical requirements (e.g., plumbing, heating, ventilation, A/C,
    etc.)
    -equipment (e.g., storage, cabinets, closets, etc.)
    -security
    -other?

    I already have most of this information but would like to be able to
    put forth a better proposal which is based, in part, on what currently
    exists. Thank you all very much in advance for your assistance. I will
    post a summary if there is sufficient response.

    John


    List of responses:

    1) From Steve Irby at the Mayo Clinic :

    Congratulations John.
    Designing new lab can be rewarding. I've taken part
    in design of 3 and construction of 2 gait labs for two different
    institutions. The disparity between design and construction is the same as
    courtship and marriage. That is, not all courtships end in successful
    marriage.

    The following are based upon my personal experience with labs that perform
    both clinical and research work.

    dimensions: 10 x 10 x 4 m, perhaps incorporate 25 m runway for
    running/throwing. Hard ceiling w/ power outlets.
    location: ground floor with nearby exterior entrance, handicap accessible,
    handicap parking nearby. Distance yourself as much as possible from utility
    power feeds, large electric motors (elevators, HVAC motors, machine shops,
    commercial refrig/freezers), radiology (MRI), and other EMI sources
    (automated teller machines can be surprisingly noisy).
    eqpt: minimally 2 force plates w/ mounting system that allows some
    flexibility without major remodelling, 6 motion cameras, 2 video cameras for
    documentation/QA. We now use camera stalks from Bogen that are monopods
    that lock in place between hard ceiling and floor. Make sure to get enough
    cable length for cameras and forceplates (your length estimate + 20%)
    function: My background includes labs with 90:10 and 20:80 clinical:research
    practices spanning 13 yrs. Design it so cables are managed (i.e. protected)
    as much as feasible. This minimized problems w/ from staff, patients, and
    visitors. Clinical application most important long term, serving
    orthopedics, rehab, neuro.
    lighting: 120 foot candles on the floor, uniform, w/ a few discrete
    adjustable intermediate levels. This makes for better video recordings, but
    seems quite bright (US standards ~70 foot candles is bright office area).
    You need power everywhere. Consider dedicated/isolated ground for EMG and
    other critical DATAQ eqpt. Beware sharing circuits w/ other areas, common
    hallways. Floor buffers will blow out circuits, other eqpt will inject
    maddening intermittent noise on ground line. We rely upon institutional
    power control which is quite extensive. Based upon local history I'd
    seriously consider UPS for critical/delicate instruments. Cost of UPS
    equipment is not too bad.
    mechanical: Heat load is primarily cpus and humans. Plan to grow 25%.
    Keep lab spaces away from water mains and drains. If heat/cooling system
    uses water, watch placement of heat exchangers overhead. Plumbing is
    cheaper up front, so if you think you might want a sink somewhere (hand
    washing or near repair shop) add it now.

    cabinetry: No one has too much, although it is often the wrong size. Make
    sure bookcase depth is adequate for 3-ring binders. Throw in a few eqpt
    cabinets (18-24" dp) to accommodate misc hardware in lab and repair areas.

    security: Needs to be discussed w/ institution. For physical security I
    like cipher locks but be prepared to change combos annually. For data
    security get backup system set up w/ off-site copies.

    other: network communication: get jacks on every wall and have them all
    connected to hub all the time. Lay out plans for data organization to
    include paper, electronic data, and video.

    Steve Irby


    2) From James Corollo at the Children's Hospital in
    Denver :

    Hi John,
    I've had the "good fortune" to design several laboratories over the past 20
    years, and feel we have found a good compromise of flexibility,
    functionality, and aesthetics at our current facility in Denver. I'd be
    happy to discuss some of the construction issues with you either by phone or
    email. No one facility design is ideal for everything you might intend to
    use the laboratory for, but if you prioritize your real needs (not your wish
    list), you can make the right choices. The design we came up with and some
    of the reasons for going this route are documented at the following URL:

    http://www.viconstandard.org/archives/2000no1/colorado/archivemain.htm

    I've developed larger facilities, but for routine clinical movement analysis
    of steady-state walking (not running), a 10 x 8.5 meter laboratory area
    gives you sufficient flexibility for bilateral 3D motion capture. Ceiling
    height should be at least 10 feet if you plan on recording high quality
    observational video, so you have the potential to use video lighting that
    projects small shadows. With this size, you can easily array 6 - 10 motion
    capture cameras around the perimeter and at different heights for whole body
    or foot models, and still achieve an adequate calibration volume of 4.5 x
    1.5 x 2 meters down the middle of the volume. While you can achieve larger
    calibration volumes with a clear 10 x 8.5 meter laboratory space using wide
    angle lenses, I generally prefer to use a normal lens focal length to
    minimize unnecessary distortions. I also like to have a separate
    "technical" area where the computers and other recording instruments (and
    the people operating them) can work without distracting the subject during a
    data capture, but not so separate that you can't easily communicate with the
    PT or kinesiologist who is leading the subject through the gait tasks. This
    area benefits from computer flooring, so the equipment interconnections are
    not exposed, and gives a slightly higher visual perspective to the
    measurement area.

    I preferred ground floor locations to accomodate force platform arrays, and
    large concrete inertial masses to mount the base plate, to achieve the
    highest natural frequency possible from the GRF recordings. We've found
    that a 1:2:1 array of 4 force platforms can accomodate most children and
    many adults referred for movement analysis. Even though our platforms are
    moveable, we rarely actually move them from this configuration to accomodate
    a clean left and right footstrike during each pass. We've used a hard
    rubber floor material on the entire measurement area (Tuflex), with a
    contrasting area defining the main kinematic lane down the center, and have
    mounted this same material to the top of each force platform. Testing by
    our manufacturer (Kistler) found that the Tufllex material dropped the
    natural frequency approximately 100Hz when it is temporarily bonded to the
    surface; from approximately 950Hz to 850Hz; still suitable for transients
    during walking.

    Electrical, mechanical, and HVAC requirements can be easily developed by the
    sub-contracted engineers assigned to the project, if you provide the
    electrical current loads and heat loads from the equipment you select. I
    prefer isolated power (no conduit grounds) for A/C powered instruments and
    computers, and separate electrical distribution for lighting and general
    office. In general, locate electrical outlets close to where the
    measurement instruments need to be, and then add more than you thought you'd
    need for flexibility, since its much less expensive to slightly overdo it
    during construction, than it is to add electrical and HVAC later.

    Best regards and good luck with your project.

    James J. Carollo, Ph.D., P.E.
    Director, Center for Gait and Movement Analysis (CGMA)
    The Children's Hospital, Denver
    Assistant Professor
    Rehabilitation Medicine and Orthopedic Surgery Departments
    University of Colorado Health Sciences Center
    1056 East 19th Ave., B476, Denver, CO 80218
    voice: 303-864-5805 fax: 303-864-5815


    3) From Alison McConnell at St. Michael's Hospital in Toronto


    hi there john!
    we're just setting up a biomechanics lab, but perhaps
    with a different focus. it sounds to me like you're planning on doing
    gait trials; we're going to be looking at trauma biomechanics, mainly
    the biomechanics of fracture fixation.

    we've got a room about 5m x 10m, with a fume hood, an Instron
    mechanical testing machine, lab benches with storage cabinets above, a
    fire cabinet, sink, freezer, and OR-style table in half the lab, and
    workstations in the other half of the lab, separated by a wall. We're
    on the ground floor of a research wing.

    hope that helps a bit!

    let me know if you have anymore questions...

    alison mcconnell


    I would also like to thank the following individuals who responded with
    documents, suggestions, contacts, etc.

    -Jim Raso from the Glenrose Rehabilitation Hospital in Edmonton
    -John Kozey from Dalhousie Univ.
    -Monika Bhuta from Innovative Sports Training Inc.
    -Norman Murphy from Tekscan
    -Stephen Cheetham from Skill Technologies Inc.
    -Gary Blanchard from AMTI
    -Edmund Cramp from Motion Lab Systems
    -Dr. Lars Janshen from the Humboldt University in Berlin

    Thanks to all!!


    John

    John M. Barden, Ph.D. Candidate
    Lecturer in Biomechanics and Motor Control
    Faculty of Kinesiology and Health Studies
    University of Regina
    Regina, Saskatchewan
    CANADA S4S 0A2
    Office: (306) 585-4629
    Lab: (306) 585-5809
    Fax: (306) 585-4854
    E-mail: John.Barden@uregina.ca

    "The value of self government at an individual level cannot be
    overestimated."

    - Frank Herbert

    ---------------------------------------------------------------